6/23/2008 12:22 AM | |
Joined: 8/10/2006 Last visit: 8/13/2024 Posts: 298 Rating: (29) |
It shouldn't do that. What is the diagnostic message inside the CPU as to why it goes into stop? |
6/24/2008 3:47 PM | |
Posts: 22 Rating: (0) |
Hi I used 2 Line Profibus-DP and 20 DP-Slave is connected to each line by bus Connector. terminator is Active only strart and end of each bus. Thanks hashemi |
6/24/2008 4:09 PM | |
Joined: 8/25/2005 Last visit: 7/5/2024 Posts: 1161 Rating: (110) |
Hello, have you loaded the OB85 as well? Havn't read it in your list. Have you seen the following FAQ? Organization Blocks of DP Master CPUs when the Distributed Periphery Fails As PCS7_id10t wrote: Take a look at the diagnostic buffer of the CPU. There should be some more information. Good luck Sabine |