4/29/2010 1:52 PM | |
Posts: 65 Rating: (1) |
Hi After an harddiskcrasch im trying to fix the new PG (PC) Having trouble to insert the new interface for S7-Simadyn DUST1. Getting an error when trying to add theinterface. (see att). Don't understand what to do next. Connection to step7/graph is ok. But simadyn using Com 1 trough DUSt 1. We have an interface that works on other PG7PC. Any idé anyone?????????? Attachmentinlopp.zip (258 Downloads) |
Last edited by: NickeNyfiken at: 4/30/2010 10:50 AM |
|
5/3/2010 5:23 PM | |
Joined: 8/31/2005 Last visit: 11/13/2024 Posts: 2198 Rating: (328)
|
To check if you have the matching versions of Step7, CFC and D7-SYS look here: http://support.automation.siemens.com/WW/view/en/22645302 If the versions are correct, you may try to use "C:\Program Files\Siemens\Step7\S7BIN\p7sdonlx.exe". This program overrides the settings in "Set PG/PC interface" for CFC. This will only help, if the driver is installed but can not be selected. Use "COMx" so set your interface. Setting"PG/PC" will restore the defaultbehaviour. AttachmentSTEP7_Compatibility_en[5].pdf (260 Downloads) |
|
|
8/20/2011 11:57 AM | |
Posts: 2 Rating: (0) |
Hi NickeNyfiken! Wonder whether you have solved this problem already and what is the solution. I am having the exact same problem now and DUST1 just wouldn't install. My COM1 is detected and available. I've tried using the p7sdonlx but still doesn't work. I've also installed SP3 for my D7-SYS V6.2 but still the same problem. Any other ideas? Meanwhile, I've forwarded my problem to the hotline but am awaiting their response. Cal. |