12/11/2007 9:17 AM | |
Posts: 739 Rating: (55)
|
Hello Gilli, according to the Parameterlist A0501 = Current Limit Cause: - Motor power does not correspond to the inverter power - Motor leads are too long - Earth faults Diagnosis & Remedy Check the following: - Motor power (P0307) must correspond to inverter power (r0206). - Cable length limits must not be exceeded. - Motor cable and motor must have no short-circuits or earth faults - Motor parameters must match the motor in use - Value of stator resistance (P0350) must be correct - Motor must not be obstructed or overloaded - Increase the ramp-up-time. - Reduce the boost. Please also check P1340 For more technical consulting please contact the Technical Support for Automation & Drives SIEMENS AG Tel: +49 (0) 180 5050 222 Fax: +49 (0) 180 5050 223 Mail: adsupport@siemens.com Support Request: http://www.siemens.com/automation/support-request Internet: http://www.siemens.com/automation/service&support FAQ : http://www.siemens.com/automation/csi_en/product |
This contribution was helpful to1 thankful Users |
1/29/2008 2:56 PM | |
Posts: 8 Rating: (0) |
hello Gilli |
6/25/2008 12:07 PM | |
Posts: 20 Rating: (0) |
Hi, When you havealarm A501, is it dangerous for theMM440 ? Thanks for your answers Best regards. |