10/16/2009 9:20 AM | |
Joined: 4/5/2006 Last visit: 10/10/2024 Posts: 917 Rating: (63) |
Hi adilmahsan , did you already checked you can browse by network the redundant server from client ? without server ask you any password? can you see OS server data confugrated in client station are in redundant mode? Is redundancy working fine? can you give more info about how you configured the station? Reagrds |
10/19/2009 8:31 AM | |
Joined: 4/5/2006 Last visit: 10/10/2024 Posts: 917 Rating: (63) |
Hi adilmahsan , seems you did everything well....just 2 question: 1) did you create a new "Guest" User or "Administrator" User? you have to create User beloging to "Administrator" & "SIMATIC HMI" Group (with same name and same password). 2) when you assigned Server Data to client station, did you get it from folder in wincc project "...\winccon\"your OS"\"Eng station name"\Packages ? if yes., can you post logs file for all station? Regards |
This contribution was helpful to1 thankful Users |
10/20/2009 7:12 PM | |
Joined: 4/5/2006 Last visit: 10/10/2024 Posts: 917 Rating: (63) |
Hi adilmahsan , 1) User had to belonging to "SIMATIC HMI"... 2) When you use Client with Project you NEED import servr data from OS Server (configuration done by Engineering Station) 3) ONLY "server data" from OS Server Master has to be import in OS Client, then check in OS client "server data" right click on "preffered server": you have to see both server staion name Regards |
10/22/2009 8:08 PM | |
Posts: 71 Rating: (2) |
thanks worked when i used the same password and username i had added a guest user earlier to access the standby server |
4/15/2014 7:53 AM | |
Posts: 340 Rating: (6) |
new question is splittet to redundant system with S7 315 CPU, "The following tags have not been created would you like to create this tag" |