5/8/2012 7:42 AM | |
Joined: 7/18/2011 Last visit: 10/9/2023 Posts: 521 Rating:
|
Hi WMingenieria , Did you try to read out module information, to find out what is cause of stop ? When is the last time that the battery is replaced? Sound like the CPU looses his program after a power outage or voltage drop. What is the position of the switch that checks the status of the batteries? Kind regards, BV |
5/8/2012 8:20 AM | |
Posts: 557 Rating:
|
Hello, save as the diagnostic buffer & share it. pls. put all diagnostic ob's. like ob121,122,85,86,87,80. you can use report system error also for the same. |
5/8/2012 2:12 PM | |
Posts: 8 Rating:
|
Hi ,, please see the file diagnostic ,, Thanks WmIngenieria
AttachmentDiagnose_03_05_2012_2.txt_.pdf (194 Downloads) |
5/9/2012 7:28 AM | |
Joined: 12/1/2009 Last visit: 9/5/2024 Posts: 672 Rating:
|
Dear WMingenieria , if you don't do any more modification on the PLC software try to use a FLASH instead of SRAM and observe the system. Regards. |
Give us your feedback and show us your respect! |
|
This contribution was helpful to
1 thankful Users |
5/9/2012 7:53 AM | |
Joined: 3/21/2006 Last visit: 9/10/2024 Posts: 10228 Rating:
|
Hello, Try it to replace the CPU in other possition in the rack. Best regards, Hristo Mihalev
|