4/15/2019 12:02 PM | |
Joined: 9/9/2015 Last visit: 6/24/2024 Posts: 727 Rating: (273) |
You gotta follow Siemens recommendation, split the drive. you gotta split it to C, D, Common Data, Transaction Log, Tags Data Group 0 , Tags Data Group 1 as per the recommendation. Attachment66579062_PH_Installation_Fujitsu_Primergy_en.pdf (578 Downloads) |
Last edited by: Jen_Moderator at: 4/16/2019 6:37:42 AMOptimized link and added PDF as an attachment. Please give me 5 stars Rating if my post is helpful for you. :) |
4/15/2019 12:24 PM | |
Joined: 8/19/2017 Last visit: 6/29/2024 Posts: 79 Rating: (3) |
I followed this manual. It does not said anything about drive configuration, Does it matters that how many drives I Should have? Does the minimum size matters? I have two RAID5 drives just like this manual!! Attachment106264271_Installation_IS_PH_en.pdf (420 Downloads) |
Last edited by: Soroosh.v at: 4/15/2019 12:25:27 PMLast edited by: Jen_Moderator at: 4/16/2019 6:39:05 AMOptimized link and added PDF as an attachment. |
4/15/2019 5:32 PM | |
Dear Soroosh.v, May be you need to create more empty drive for the checking to pass through? |
4/23/2019 2:03 AM | |
Cool, thanks for sharing. So now you just configure 3 drives right? 1. Operating system and sofware 2. tranc Log 3. Historian database Three drives? Is your problem resolved? Then you might need to create information server in another machine right? |
6/3/2019 9:34 AM | |
Joined: 5/3/2017 Last visit: 5/21/2024 Posts: 673 Rating: (217) |
Hi Soroosh.v, Which RAID drivers do you use? The recommended RAID drivers for SIMATIC PCS 7 industrial workstations can be found in the FAQ Which RAID drivers are recommended for use on SIMATIC PCS 7 industrial workstations?. With regards |
