Industry Online Support
Technical Forum
3/21/2008 12:57 PM | |
Joined: 9/27/2006 Last visit: 9/4/2024 Posts: 12282 Rating:
|
Hello Profimus; Look for the manual S7-300 Module data: http://support.automation.siemens.com/WW/view/en/8859629 Chapter 5 explains the different ranges and numerical representation of analog input modules with different measuring ranges. For evxample: for RTD modules, you will read 0,00 or 0,0 (depending on the specifics of your RTD) for 0 Celius; 130.00 for 130 degrees Celius; -25.00 for -25 degrees Celsius. If they are wired and configured properly. I don't think it should be too difficult. Chapter 6 gives details for each type of analog module for the S7-300, including wiring and configuration data. Hope this helps, Daniel Chartier |
3/21/2008 1:53 PM | |
Posts: 27 Rating:
|
Thanks for your help, this will certainly help me. Next mondayI will be testing so I will post the result. |
3/26/2008 3:29 PM | |
Posts: 27 Rating:
|
Tested the PT100's today and it worked! Thnx again! |