hi Riko, as I can see on A1000 Drive Profibus-Interface is an optional feature. Does yours have that Interface? What connector does it have? Is there no manual to read out how to connect it? regards, |
FCK WAR! |
|
6/11/2015 10:59 AM | |
Posts: 35 Rating:
|
Hi all.. Is it possible for me to connect my profibus cable with RS232 then connect it to my PC so that I can extract the data from it? Thank you. |
6/11/2015 2:06 PM | |
Joined: 9/27/2006 Last visit: 2/20/2025 Posts: 12339 Rating:
|
Hello Riko; Quick answer: no. Profibus is designed on a RS-485 electrical standard, not RS-232. The interfaces are different, the transmitter electronics are different, the supported voltage levels of the signals are different, the signal pinout is different, the cable characteristics are different... Basically, you cannot use RS-485 cable on a RS-232 interface and hope to transmit data properly. I suggest you start looking for basic information on the subject so you understand what you are asking. For example: What's The Difference Between The RS-232 And RS-485 Now, if you have an RS-232 port on the Yaskawa drive, an RS-232 port on your computer (or possibly a Rs-232/USB cable) and a software on the PC that can read the Yaskawa drive information through the RS-232 connection, then maybe you can use an RS-232 cable between the drive and the PC. Or simply use the Profibus cable and connectors to interface the PLC and the drive... Hope this helps, Daniel Chartier |