1/30/2009 11:24 AM | |
Posts: 2930 Rating: (432)
|
Hi, S7-200 do not support Profibus DB Master. regards |
1/30/2009 11:34 AM | |
Posts: 16 Rating: (0) |
Sorry fried, i have not mentioned type of cpu. it is not S7-200 CPU, i have talking about S7-300 that also 319-2DP CPU, in that i don;t want to use MPI Port. |
1/30/2009 1:24 PM | |
Joined: 9/27/2006 Last visit: 11/11/2024 Posts: 12293 Rating: (2691) |
Hello muttu; If I understand correctly, you want to have the CPU in the middle of the network, not at an extremity? Easy to do with any tyoe of Profibus-certified connectors. You can buy them from Siemens, Phoenix Contacts, and many other manufacturers. The following attachment shows how you can use a typical Profibus connector either at the cableend (with terminator ON) or in the middle of the network, as you wish to do. Simply makesure that the terminator switch is OFF when connecting to any node in the middle of the network, and ON at both ends. Hope this helps, Daniel Chartier Attachmentprofibus_connector.pdf (196 Downloads) |
2/1/2009 1:46 AM | |
Posts: 5822 Rating: (412)
|
Hello, for further information's on SIEMENS PROFIBUS Connectors please check this document out: |