10/5/2017 8:51 AM | |
Posts: 10 Rating: (0) |
Hello, We are in an installation with S7-300 CPU319F System and ET200S With Safety Integrate Modules. At sporaidic times, 3 PROFIsafe PM-E F pp 6ES& 138-4CF42-0AB0 modules, in 3 different stations returns a module fault. In IM151, it reads, "Faulty Module(diagnostic interrupt detected), External Error" Further help on error says, Error with various causes, & Remedy depends on cause. In diagnostic byte during that fault, is DEC 16 = BIN: 0001 0000 It asks for acknowledgment, but we are not able to acknowledge the fault, or we are not doing it in a proper way. We have the program to acknowledge for "reintegration", which works. We do need some help on this. Attached are some screenshots of the faults and status.
AttachmentPME Fault.zip (116 Downloads) |
10/6/2017 5:23 AM | |
Posts: 5 Rating: (0) |
1.check your connections are properly done at modules end 2. your hardware configuration has matching are not 3. all the address are properly assigned are not . |
10/6/2017 7:26 AM | |
Joined: 3/5/2014 Last visit: 8/5/2022 Posts: 5521 Rating: (1054) |
hi, have a look in the manual of the module: SIMATIC Distributed I/O System Fail-Safe Engineering ET 200S Distributed I/O SystemChapter 7.3.5 are the diagnostic functions of the module 1hex means: short circuit. Cross-circuit between P1 and L+. Remedy the cross-circuit and acknowledge the error within 100 hours after the error has occurred. or internal error. Replace the module. hope this helps, regards, |
FCK WAR! |
|