Joined: 4/10/2006 Last visit: 7/14/2024 Posts: 921 Rating: (2) |
Hallo... I have a problem with comunication from pc and op17... I transfered proget with protool software version 6.0 sp3... For this, i use one pc with adapter usb ----> RS232 and setting as com2.... Download this proget is ok until some time but, after some minuts, on the monitor pc appears one error (see attachment).... Can you help me? I need urgently solved this problem... Thank you Roby Attachmentop17_error_comunication.pdf (233 Downloads) |
Setting of my PG M6 Siemens |
|
8/15/2008 7:34 PM | |
Posts: 3149 Rating: (171)
|
Hello, please check the FAQ e.g., search for "protool transfer error" http://support.automation.siemens.com/WW/view/en/15178263 nemo |
8/25/2008 10:47 AM | |
Posts: 220 Rating: (14) |
Hi Roby, yes you'll need an 9pin serial-interface (25Pin also works its then the cable pinout 6XV1440-2L). See following Link Appedix C: http://support.automation.siemens.com/WW/view/en/1405528 Make also sure that your desk has an real RS232 Interface, some manufacturer meanwhile has inside only USB and build an "internal USB-RS232-Interface". Sometimes the USB-RS232 is possible and can be used for download to OP17, but its not released, because it not sure that its work again or every time. On is nearlysure when it don'twork it will never work with this panel and this desk. The problem is often little differences in the elements inside... regards Aranel |