8/9/2021 12:24 PM | |
Joined: 4/24/2006 Last visit: 10/14/2024 Posts: 8745 Rating: (1168) |
Hello, Have a look at the following manual: SIMATIC S7-300 SM331;AI 8x12 Bit Getting Started Part 2: Voltage and PT100 See paragraph 5.2.3 Best regards, Wizard |
10/12/2021 10:45 AM | |
Joined: 3/5/2014 Last visit: 8/5/2022 Posts: 5521 Rating: (1054)
|
hi azizmustofa8, When you using a converter, you are measuring the current from the converter, not the PT100 itself. I assume the converter has an additional power-supply. that means you have a 4-wire-transducer (2wire for measuring, 2wire power-supply). set your measurement range module to C. wiring is described here: Analog input module SM 331; AI 8 x 12 bit;(6ES7331-7KF02-0AB0) hope this helps, regards, |