2/21/2018 8:48 AM | |
Joined: 4/28/2015 Last visit: 10/30/2024 Posts: 10585 Rating: (825)
|
Hello, what exactly HW cfg is on S7-300 side? Ports, CPs, ... |
With best regards... |
|
2/23/2018 10:29 AM | |
Posts: 7 Rating: (0) |
CPU 313C-2 DP Thank you |
3/6/2018 12:57 PM | |
Joined: 4/28/2015 Last visit: 10/30/2024 Posts: 10585 Rating: (825)
|
Hello, maybe question is how much data you need transfer. In my opinion: 1. you can attach DP Master module to S7-1200 and try configure some user defined I/O area and coordinate data with S7-300, here need to be S7-300 defined as DP Slave. I see here also fill I/O area with S7-300 programatically. 2. you can attach DP Master module to S7-1200 and try configure some S7 connection with S7-300 DP port. It need to be investigate further if S7-300 can use that integrated port as S7 server. 3. Maybe some FDL data exchange can be created also. Look to this manual: CPU to CPU communication |
Last edited by: Duris_I at: 3/6/2018 12:59:53 PMWith best regards... |
|