4/9/2012 12:44 PM | |
Joined: 10/7/2005 Last visit: 10/13/2024 Posts: 3024 Rating: (1054)
|
Hello MrBin it depends on a number of things if youcan use a6ES7431-0HH00-0AB0 as a replacement for a6ES7431-1KF00-0AB0, but it will generally NOT be an easy straightforward swap andwill also require a fair bit checks, HW config changes,and re-wiring. Have a look at the technical spec of both cards and you'll see that 0HH0 is a 16 channel non-isolated AI card which caters for Voltage and Current AI's, wheras your existing1KF00 is an 8 channel optically isolated AI card which for Voltage, Current and Resistance AI's. Providing you do not need the isolation feature nor have any Resistance AI's in use, you are still facedwith a different pin layout (i.e. re-wiring of the front connector is required) andalso need to change your HWconfig, so it is not a straightforward swap. I hope this helps |
Cheers |
|
4/23/2012 2:51 PM | |
Posts: 90 Rating: (0) |
Thanks everybody! I repaired. |