1/9/2015 2:38 PM | |
Joined: 1/28/2009 Last visit: 5/20/2024 Posts: 6840 Rating: (1359)
|
Yes , it is possible to change the back up batteries while the PS is ON.Follow the instructions in "7.1 Replacing the Backup Battery" of the following manual:
Automation System S7-400 Hardware and Installation |
This contribution was helpful to2 thankful Users |
1/9/2015 2:40 PM | |
Joined: 9/27/2006 Last visit: 6/4/2024 Posts: 12260 Rating: (2670)
|
Hello Gaston; From a note in the S7-400 module data manual, discussing the battery option on the power supply mdules (both AC and DC), it seems they recommend having the power supply installed and powered when installing thew batteries. See the attachment, taken from this link: SIMATIC S7-400 S7-400 Automation System Module Data Hope this helps, Daniel Chartier |
This contribution was helpful to2 thankful Users |
5/27/2020 9:08 AM | |
Joined: 12/10/2018 Last visit: 5/26/2024 Posts: 109 Rating: (11) |
Hello Dear Gaston_Sanchez As long as the power supply module is under load (Is On), you can replace the batteries The attached file provides comprehensive information on how to install and use the battery.
AttachmentS7-400 Backup Battery.pdf (582 Downloads) |