Hello Srihari, There is a logical reason (process control perspective) behind CountOH faceplate not having the operator reset button in a predefined manner. Hence, the option to reset it (internally) via logic/block level makes more sense. However, if you still want to go ahead and configure it one of these ways: - The easier method is to define 0d , 0m and 0h in the Preset values and use the Preset button, to 'reset' your counter. (This is just a workaround using the functionality of preset to reset if at all you are not using the actual preset function) - In the block level, there is an Input parameter 'Reset' in the block which can be triggered (and the feature bit 30 as rightly mentioned by you) - The other method will involve faceplate customization -> There are multiple links in one of the posts in this thread with links to help you perform block icon and faceplate customization. LINK Also, check out the APL Style Guide manual attached with this post for further information. AttachmentPCS7_APL_Styleguide_en_EN_en-US (2).pdf (130 Downloads) |