11/29/2018 4:19 PM | |
Joined: 12/18/2014 Last visit: 12/2/2023 Posts: 31533 Rating:
|
It is better if the original STEP5 program is available. |
11/29/2018 4:51 PM | |
Joined: 12/18/2014 Last visit: 12/2/2023 Posts: 31533 Rating:
|
That was the reason for my first answer ... |
11/29/2018 4:57 PM | |
Joined: 1/25/2016 Last visit: 11/21/2023 Posts: 14 Rating:
|
Here you go. Thank you.
AttachmentS5 PLC program.zip (89 Downloads) |
11/29/2018 5:05 PM | |
Joined: 12/18/2014 Last visit: 12/2/2023 Posts: 31533 Rating:
|
Do you know, which S5 type you have? S5-115U? Or S5-135U? Or other? |
11/29/2018 5:24 PM | |
Joined: 1/25/2016 Last visit: 11/21/2023 Posts: 14 Rating:
|
I just checked the picture from the project. It is an 115U |
This contribution was helpful to
1 thankful Users |
11/29/2018 6:08 PM | |
Joined: 12/18/2014 Last visit: 12/2/2023 Posts: 31533 Rating:
|
I insert the FBs (FB250 and FB251) in your program. This FBs are FB in firmware of the PLC. FB250 = Reading and Scaling an Analog Value. This are Standard-FBs from Siemens and can't convert to S7. AttachmentKALKLO.zip (107 Downloads) |