And why post you this in the S7-200 conference? |
1/3/2022 7:18 PM | |
Joined: 9/27/2006 Last visit: 7/14/2024 Posts: 12268 Rating:
|
Hello Gyuri; There are no S7-1200 Namur input modules available. There are Namur input modules for the S7-1500 and Et 200MP: https://support.industry.siemens.com/cs/us/en/view/109798607 Since the ET 200MP stations can become IO device stations over Profinet, with an IM 155-5 PN as head module, they could be configured as part of a Profinet IO system where the S7-1200 acts as a IO controller. Hope this helps, |