Hello Pease I have 6es7 157-0aC82-0xa0 coupler can I use it with S7 1200 (Profibus Master) to reeceive data from Profibus PA Slave ? Thanks ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 02/27/2023 10:53:34New subject after splitting |
|
2/27/2023 11:06 AM | |
Joined: 9/27/2006 Last visit: 9/7/2024 Posts: 12282 Rating: (2682)
|
Hello kamal; If you have set up your CM 1243-5 Profibus master module correctly in your hardware configuration, then yes, you can add Profibus/PA instruments on the Profibus network. When you work with a DP/PA coupler, there are à few points you must take into account. First, the DP/PA coupler is not configured on the Prfibus network (in hardware configuration): i is transparent. You need to isetup only the instruments, once ther gsd file has been integrated. as if they were Profibus-DP slaves. Then, the overall speed of the Profibus network must be reduced to 45,45 kB, for all slaves. https://support.industry.siemens.com/cs/ca/en/view/109771783 Next, when you configure each slave in the hardware configuration you will find out that the data exchange for each one is limited to 5 bytes: one Real (4 bytes) register for the instrument's measured value and one status byte to detail diagnostic information of the slave. Hope this helps, Daniel Chartier |