Does anyone know where to find the suggested torque ratings for screw terminals on S7-1200 and its modules? |
1/27/2011 10:03 PM | |
Posts: 13 Rating: (1) |
Hello, I don't think that such informations exist anywhere. |
1/28/2011 10:17 AM | |
Joined: 9/23/2005 Last visit: 11/14/2024 Posts: 4352 Rating: (1452)
|
Hi, in the S7-1200 manual (http://support.automation.siemens.com/BR/view/en/36932465), chapter 2.3, topic "Guidelines for wiring the S7-1200" stay: " All S7-1200 modules have removable connectors for user wiring. To prevent loose connections, ensure that the connector is seated securely and that the wire is installed securely into the connector. To avoid damaging the connector, be careful that you do not over-tighten the screws. The maximum torque for the connector screw is 0.56 N-m (5 inchpounds). |
Denilson Pegaia |
|