Hi guys, I need your help for diagnostic buffer error ID 16# 06:4040 Error: Error on partner - No neighbor could be detected and 16# 06:4000 Error: Data transfer not possible - Connection error - connection interrupted. Hardware specific: S7-1511F (6ES7 511-1FK02-0AB0), Firmware v2.6.1, Tia V15.1 project version. The system consist of 3 encoders connected to the MRP ring redundacy via scalance swicth managed XB216 on port 1 and 2, the network works fine but sometimes these alarms on buffer appears, and i'm not be able to understand if is a device problem, wiring problem or wrong configuration. I setup the switch parameters and the hardware configuration for the MRP ring in according to the user manual "109739614_MRP_DOKU_V10" from siemens. the wirings have been verified and are ok. Any tips to help me? Regards |
Last edited by: Jen_Moderator at: 10/10/2023 07:09:46Link embedded from manual. |
|
10/4/2023 10:11 AM | |
Joined: 9/23/2005 Last visit: 10/4/2024 Posts: 4349 Rating: (1446)
|
Hi, It seems something related with the topology monitoring. I suggest you (if possible) to update the CPU Firmware https://support.industry.siemens.com/cs/br/pt/view/109476729/en It should not solve the problem, but should be possible that improve the diagnose. If possible test to load the project with and without the topology definitions, and check if there are differences in the behavior. |