i need an urgent help from anybody.... i am work on S7-300 CPU 319-3 PN/DP and i face a big problem "now i download the program and hardware configuration) Now "CPU RUN but all modules have SF & BF faults also CPU have "I/O access reading error") For information i am using profibus network including repeaters and i attach the congiguration & print screen online" Thanks alot for fast reply & cooperation Attachmentconfiguration.zip (90 Downloads) |
12/16/2012 2:35 PM | |
Posts: 7 Rating: (0) |
the right position for switches i mean the "on/off'" switches not the address one |
12/16/2012 3:43 PM | |
Joined: 12/22/2006 Last visit: 1/25/2022 Posts: 1742 Rating: (308) |
Hello, See document in annex. Where you see a check mark, close the termination Where you see a "O", let it open. Be aware that for the connectores where the termination is ON, the cable must be connected on the side with the incoming arrow. AttachmentD:\Temp\PB termination.pdf (68 Downloads) |