Hi WillemJakobs, This is because the CP343-1 only supports Lean PUT/GET when it is acting as a server, not as a client. But in terms of S7 communication with PUT/GET, the server is the passive part where you do not configure a connection. Kind regards |
7/16/2024 1:01 PM | |
Joined: 3/20/2013 Last visit: 10/23/2024 Posts: 44 Rating: (1) |
I already had such a suspicion, thank you for the confirmation.
|