Hello Sandeep; You can use GET/PUT functions (FB15, FB14) on the S7-300 to send and retrieve data to/from the S7-400 without any modification or programming on the S7-400. The only limitation is the amount of bytes of data you can transfer (76 bytes both ways, on a S7-300, if I remember well). See the following document for guidance: https://support.industry.siemens.com/cs/us/en/view/18610307 Hope this helps, |