Hello Sifmfns; I hope you realize that troubleshooting a gateway is always more complex than a direct connection from the PLC (setup as a Modbus master, for example). Let's say that your configuration of the ADFweb station is correct, your Profinet parameters are registered, your Modbus parameters have been all setup properly with the OMRON slave; what addresses (Modbus) in the slave are you using to read the temperature values from? If these are incorrect, even if the whole communication link is perfect, your watch table will come up empty (or with values 0). Manual of the gateway: http://www.adfweb.com/download/filefold/MN67602_ENG.pdf So you have to check: - the Profinet side of the gateway (IP address and Profinet name of the device) -the Modbus master side of the gateway (address of the Modbus master and slave, communication parameters, RS 485 wiring) - the Modbus addressing of the values you want to read in the Omron slave First, what LEDs are active on the gateway, the S7 PLC and the Omron slave? Do no simply state that none are active, some of them are designed to be lit whjen the units are active. Some provide diagnostic information, which is what we are looking for. Second, how have you configured the communication links in your project? For the gateway, screenshots of your Compositor software settings would be useful. The ADFweb manual has a section on Modbus diagnostics (and advanced functions) and a chapter on PLC configuration, shown with TIA Portal. Is there any information there that can be helpful to troubleshoot your problem? If you want to show us your project information, since you cannot attach more than one screeshot per post, I suggest you collect them in a Word or pdf document and attach that to the next post in this thread. Hope this helps, Daniel Chartier |
This contribution was helpful to1 thankful Users |
6/19/2020 2:52 AM | |
Posts: 17 Rating: (2) |
Here is my project. AttachmentNew Microsoft Word Document.docx (220 Downloads) |
6/19/2020 3:02 AM | |
Posts: 17 Rating: (2) |
There is no any error on network. GSD installed, Compositor settings updated to HD67602. |
9/22/2020 9:08 AM | |
Joined: 2/6/2020 Last visit: 11/13/2023 Posts: 2 Rating: (0) |
|
Follow us on