Hello, Read the manuals and clippings below: SIMATIC Distributed I/O System Fail-Safe Engineering ET 200S Distributed I/O System ********** Spare parts case for a fail-safe module You can replace a fail-safe module by a successor module with a higher order number. The new fail-safe module takes on any existing configuration and then behaves like the replaced fail-safe module. Remember to Set the PROFIsafe Address When replacing fail-safe modules, ensure that the address switch (DIP switch) setting of the new fail-safe module is identical to that of the replaced fail-safe module. SIMATIC Industrial Software SIMATIC Safety - Configuring and Programming ********** Replacement of hardware components Hardware components for SIMATIC Safety (F-CPU, F-I/O, batteries, etc.) are replaced in the same way as in standard automation systems. Also read the topic below: CPU-F red SF after replacing the fail-safe module Eventually:
|