8/1/2013 6:35 PM | |
Joined: 9/23/2005 Last visit: 9/25/2024 Posts: 4347 Rating: (1446)
|
Hi, one of the inovations of the SP1 for STEP7 V12 (Released for Delivery at http://support.automation.siemens.com/WW/view/de/76276623) is the possiblity to simulate someCPU to CPU communication.
Once GET PUT communication is very popular, I post here a sample program about it. TIP: Diferently to S7-200, 300, 400 and 1200, it is necessary to set in theServer CPU the CPU property: "Protection -> Connection mechanisms -> Permit access with PUT/GET communication from remote parter (PLC, HMI, OPC, ...)" to enable this type of communcation Note: thanks to Mr. Andreas Hoho for the TIP AttachmentC:\Users\z0008iwv\Documents\Bluetooth Exchange Folder\GetPut.zip (6658 Downloads) |
Denilson Pegaia |
|
This contribution was helpful to6 thankful Users |
11/4/2014 11:01 AM | |
Joined: 4/7/2014 Last visit: 6/22/2021 Posts: 40 Rating: (0) |
Hi Pegaia, I'm trying to send data, with the PUT function from a S7-1500to a S7-400 PLC, but its not working. Can you make an example programm for that as well? I'm getting the failure: Greetings, Paul AttachmentComm_PUT_Error_Faulty.pdf (3073 Downloads) |
11/5/2014 9:22 AM | |
Joined: 4/7/2014 Last visit: 6/22/2021 Posts: 40 Rating: (0) |
Hi Autogen, Do you use two S7-1500 PLC's or one S71500 and one S7-400? Greetings |
12/23/2014 10:08 AM | |
Joined: 9/23/2005 Last visit: 9/25/2024 Posts: 4347 Rating: (1446)
|
Hi, it is a pleasure to help you! :) |
Denilson Pegaia |
|