3/27/2010 9:38 PM | |
Posts: 3 Rating: (0) |
Hello, Kind of a newbe question, We have a pressure sensor with a range of 0-16bar, output is 4-20mA How can i get a proper reading value since input only can be set to 0-20ma I already used this linkhttp://support.automation.siemens.com/NL/llisapi.dll?func=cslib.csinfo&objId=39334504&objAction=csOpen&nodeid0=34612486&nav0=tree&lang=en&siteid=cseus&aktprim=0&extranet=standard&viewreg=NL I cann't understand what is happening here look at MW10 and MW40 value's are the same? can anyone help please thanks
|
Last edited by: qlip at: 3/27/2010 9:39 PM |
|
3/28/2010 2:24 PM | |
Posts: 30 Rating: (0) |
How about a Norm with Min @ 5536, and max @ 27648. Feeding a Scale with min @ 0.0 and max @ 18.0 ? |
3/28/2010 7:10 PM | |
Posts: 3 Rating: (0) |
Ok will try tommorow, Do you have a meaning with the 18 value? max range of the sensor is 16bar? thanks |
3/29/2010 12:35 PM | |
Joined: 9/23/2005 Last visit: 11/14/2024 Posts: 4352 Rating: (1452)
|
Hi, there is a ready to use blocks for 4..20mA on /tf/WW/en/Posts/31698#150327 |
Denilson Pegaia |
|
3/29/2010 8:37 PM | |
Posts: 3 Rating: (0) |
5530 @ MIN on the normX block did the trick. I will take a look on the "ready" block of Pegaia tomorrow. thanks Again |
3/30/2010 12:14 PM | |
Joined: 9/23/2005 Last visit: 11/14/2024 Posts: 4352 Rating: (1452)
|
Hi, just one alternative more: http://support.automation.siemens.com/WW/view/en/42087579 |