Hello, you have to use WRIT_DBL Restart: Changes to the start value in the load memory are made using the extended instruction "WRIT_DBL" (write to DB in load memory). Changes will not take effect until after restart of the technology object. 8.2.3 "Simulation" tag (positioning axis) (S7-1500, S7-1500T) The tag structure "<TO>.Simulation.<tag name>" contains the configuration of the simulation mode. In simulation mode, you can simulate axes without a real drive in the CPU. ..... https://support.industry.siemens.com/cs/ww/en/view/109781849 Before disconneting the motor, you have to park the drive, via control word in MC_PostServo. |