9/19/2008 4:18 PM | |
Posts: 487 Rating: (45) |
It is not possible to use profibus to link two S7-200 PLCs. The profibus module available forS7-200 is EM227which can only be a profibus slave. You need a master in the network. So this is not possible unless you have some other master in the network. For communication betweenS7-200 PLC, you can either use PPI network which is available on CPU. Or you can use CP243-1 to do it over ethernet. Check the following links http://support.automation.siemens.com/WW/view/en/41561 https://www.automation.siemens.com/microset/ftp/tipstricks/t27-e.zip Again, you talkedaboutinterfacingTP to PLC via profibus. This isalso not possible. You can use EM277 as MPI slave and connect TP to it. Or are talking about connecing to TP from CPU port using a profibus cable? In this case, you are not using profibus network, it is still a PPI interface. You are just using profibus cables and connectors beacuse physically they are both RS-485 |
9/22/2008 9:10 AM | |
Posts: 116 Rating: (1) |
I think you can use MPI connection to communicate between two CPU's |