Joined: 3/14/2008 Last visit: 7/25/2024 Posts: 2079 Rating:
|
Hello, You can use the following parameter: OPTIPNO in the Note texts characteristic In a step you can set on initialization step: OPTIPNO = 1. This will prompt the operator in the sfc type. The comment can be set in the characteristics. The operator has toacknowlegde the popup.The operator action check happens in the transition In the transition set the condition: OPTIPNO = 0 AND if a setpoint is entered. PS:After acknowledge by the operator, the optipno is set to zero so that is your transition condition The setpoint you can do as follows: Write entered setpoint to a temp (bit memory). Equal the output setpoint to the bit memory variable and in next step clear the bit memory.. In the transition with the OPTIPNO=0 add an AND condition where you say "output setpoint = "temp variable". There are other ways, but this is what I can think of right now. |
Last edited by: Oreca at: 2/4/2013 9:04 AMIf I could help you, you can use the RATE button. Thank you. |
|
2/4/2013 4:52 PM | |
Posts: 20 Rating:
|
Thanks Oreca, Just what I was looking for. |
2/4/2013 9:01 PM | |
Joined: 3/14/2008 Last visit: 7/25/2024 Posts: 2079 Rating:
|
Glad I could help |