Hi, you don't mention if you are controlling these by PLC or digital, but I will assume digital, otherwise the question makes no sense. There are free function blocks available, if you look in the MANUAL, there are three ON-Delay timer blocks available (See section 8.3.14.14) that you can trigger to do various things with i.e. switch in a different setpoint RPM after x minutes, using the numerical switch blocks also available (see section 8.3.14.17) Regards, Graeme |