6/25/2010 7:13 PM | |
Joined: 9/18/2006 Last visit: 5/3/2024 Posts: 589 Rating: (64) |
Hi. This small addition. Possibly - I2t axis limiting responds. I hope it to you will help. Best regards. AttachmentI2t pre–warning and motor temperature monitoring.pdf (787 Downloads) |
Last edited by: pfuser at: 6/25/2010 7:15 PM |
|
6/26/2010 6:06 AM | |
Posts: 2964 Rating: (479) |
Hello... Could you check the I/R module spearately by disconnecting the other modules..... if you have used drive ready input 73.1 and 73.2 check it out.... check your head stock motor is creating a load that why DC voltage is getting indicated on the I/R module.Disconnect this particular module and try to check.... I am attaching you the checking procedure which is already present in the fourm... Hope this information will be useful. Ekalavya. Attachmentchecking steps for IR module.pdf (748 Downloads) |
This contribution was helpful to2 thankful Users |