1/10/2018 4:42 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (876) |
Hello, Please download 6RA22 drive manual, refer chapter 5 Start up. Follow the steps as explained to enter motor related parameters in respective fields, ( no optimisation is possible).Connect toggle switches to apply CR & drive start commands at X1:18 & X1:17 respectively. Connect X1:23 to X1:24 so that +10 V refernce voltage will be applied. Set P76 = 1 i.e. external field applied since in your case no motor is connected. Refer circuit diagram on page 31 to 33, depends upon your supply voltage levels & drive specification. Connect power to contactor, two phase at X2:2U & 2W terminal, connect two lamps atleast 100W rating inseries across DC output terminals, 1C 1D. Apply control enable & drive commands, you should get maximum DC voltage at DC output terminals & lamps should glow. HTH. |
This contribution was helpful to1 thankful Users |
Follow us on