Hi, I mean the blocks in the library "Failsafe Blocks (V1_2)" and then in the directory "F-Simulation Blocks". The blocks are overwritten by those blocks, see the handbook "Safety Engineering in SIMATIC S7" behind the link: http://support.automation.siemens.com/WW/view/en/22098643 |
I hope that the answer will help, if you have still questions, don't hesitate to ask me. |
|
7/3/2007 2:25 PM | ||||
Joined: 5/18/2006 Last visit: 10/21/2020 Posts: 170 Rating: (64) |
With PLCSim V5.2 the F-Simulation blocks are no longer required. However, in order to simulate an F-Program the HW config must first be downloaded to the PLCSim (with password 'plcsim'). This tells the PLCSim to act as an F-Controller. Once the HW is downloaded, the CFC (with normal F-Blocks) can be downloaded and go online. Reference:
5.4.10 Testing a Safety Program Offline with S7-PLCSim |
|||