9/5/2008 10:00 AM | |
Posts: 139 Rating: (25) |
one place to start to get a general drift of what telegram to use is page 348 of the S120 function manual https://www.automation.siemens.com/doconweb/ this describes thesome of thetelegrams that are available and their general application. Then the next thing you can do is in starter in the project tree you can open up the main configuration page and in here select the different profibus telegrams. then clicking on the message conffiguration button with a units telegram selected will take you to where the message is defined. play around with this until you are familiar with the different telegrams and then make your choice. If it is an integrated project you will also have the option of synchronising the project with the PLC hardware config from the main starter configuration page. otherwise you will have to do it manually in your PLC project aswell. does this make sense? |
Last edited by: Anchobi at: 9/5/2008 10:07 AMadded link |
|