6/12/2014 3:32 PM | |
Joined: 9/27/2006 Last visit: 7/14/2024 Posts: 12268 Rating: (2675) |
Hello Kevvie; Sinec L2 is not directly compatible with Profibus-DP, being a pre-existing protocol supported only by Siemens equipment. But many later Sinec L2 porocessors came with an option "DP-Standard" which allowed them to work with Profibus-DP masters, with some restrictions on the bus speeds (generally up to 1,5 MB) and data exchange limitations. This last should be no problem in the case of a Siemens drive using PPOx configurations, as this limits the number of bytes for each cyclic data exchange with the Profibus-DP master. As you can see in the following extract from a Masterdrive manual (see the attached screencapture) the CB1 accepts Profibus-DP configurations: 12 Guidelines to changeover from CB1 to CBP - Siemens You probably shall need to integrate the CB1 in your Step 7 Profibus Configurator (in HWConfig); you can find the required gsd file (SIEM8022,gsd) for the CB1 as a Profibus-DP slave in the following link: PROFIBUS GSD files : MASTERDRIVES Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 6/12/2014 3:33 PM |
|
6/12/2014 3:54 PM | |
Joined: 1/21/2013 Last visit: 6/6/2024 Posts: 4620 Rating: (705) |
Hello Kevvie, in addition to what he wrote our expert dchartier take a look to other experts if it can help you: Sinec L2 DP with Profibus DP:: URGENT - Siemens Industry Online ... |
6/12/2014 9:26 PM | |
Joined: 9/27/2006 Last visit: 7/14/2024 Posts: 12268 Rating: (2675) |
Hello Kevvie; In the sense that the CB1 only allows cyclic communications (and diagnostics)betwen master and slave, you could say that it is a DPV0 Profibus slave. Here are some presentations on the same subject, first from the Siemens forum: Difference between DP V0, DP V1 and DP V2 and from Profibus.com: What are the differences between PROFIBUS V0, V1, and V2? Hope this helps, Daniel Chartier |
This contribution was helpful to1 thankful Users |
Follow us on