11/25/2010 12:27 PM | |
Posts: 2964 Rating:
|
Hello.... Have you provide the 24vdc supply for the USB? document is attached for the reference Looks like NC-PLC need to be cleared and check? Any alarm message on the Operator panel.... Regards, Ekalavya AttachmentPC_Adapter_USB_e.pdf (432 Downloads) |
Last edited by: Ekalavya at: 11/25/2010 12:43 PMdocument attached |
|
11/28/2010 4:47 PM | |
Posts: 7 Rating:
|
Dear Sir, Thanks for the information. i tried using Simatic PG with HMI adance V7.1 &V7.2, but unable to establish a communication. Always a message on Laptop . No connection NC/PLC.120202. overall reset is done for NCK and PLC. The dispalyon the OP is there , butPLC still in stop mode. would you advice me the pin out cable connection for loading through win PCin. is it possible to load the archive files from Winpcin. Pls see attached datas. thanks for all the support. Regards, AHK AttachmentALMUTLAK.zip (322 Downloads) |
11/28/2010 6:25 PM | |
Posts: 2964 Rating:
|
Hello.... Where are you plugging the cable X122 / X101 You should plug the cable in X122. If you are using the HMI advance Version 7,1 and 7.2 in your PG, < There is some thing called NCU Wizard connection in that you need to select SINUMERIK 840D Powerline > In this make selection slow MPI on X122... > Once you open your HMI goto Startup>HMI>Operator Panel> Ensure you have kept the address proper NCK(3) and PLC(2) if this address is kept HMI ahould Communicate. Check it out..... You can load the Archive files through WINPCIN....attaching you the link /tf/WW/en/Posts/42750#top Check it out.. Regards, Ekalavya |
11/29/2010 2:28 PM | |
Posts: 2964 Rating:
|
Hi... You can try not a problem both side should be same.... Could you keep S4 to position 2 and then load the backup. Regards, Ekalavya |