Hi all, I am using 3TK2826 1BB40 SIRIUS Safety Relay. In Safety relay Device LED indication will be red after pressing E-Stop every time. After that I have to power reset then relay will be healthy. What is the problem and how to resolve this problem. Some details given below. E-stop = 1 Sensor with 2 NC contact I have also adjusted the DIP switches according to configuration. Kindly reply asap. Thanks.
---------------------------------------------------------------------------------------------------- |
Last edited by: Min_Moderator at: 4/29/2015 4:12:20 PMNew subject after splitting |
|
11/11/2017 4:00 PM | |
Joined: 9/15/2015 Last visit: 7/1/2024 Posts: 67 Rating: (6) |
please check input signal in example circuit in manual, input shoud be activated stimulately |