5/21/2011 8:28 PM | |
Posts: 259 Rating:
|
Hi, I have problem with SITOP 6EP1 437-3BA00 Input AC 500V Output DC 24V/40A. Before this power module I have on each phase fusible 20A they are burned. I put new one I disconnected outputs cables and switch main power on immediately fuses was broken. I check cables between fuses and sitop and everything was all right. I dismount module take out cover but I don't see any visible damage. Maybe someone have similar problem with this module... With regards, makaveli AttachmentSITOP.zip (244 Downloads) |
5/21/2011 9:02 PM | |
Joined: 5/28/2008 Last visit: 7/17/2024 Posts: 4511 Rating:
|
Hello makaveli, To avoid this problem, I recommend to follow the data sheet of the power supply by connecting a minuture circuit breaker on the inputs with the following specifications: 3-pole connected miniature circuit breaker 10 ... 16 A characteristic C or circuit breaker 3RV1021-1DA10, setting 3 A or 3RV1721-1DD10 (UL 489) Here'slinkof the Power supply specifications. Hope this helps.
|
Last edited by: Ayman Elotaify at: 5/21/2011 9:42 PMAyman Elotaify |
|
5/21/2011 9:14 PM | |
Posts: 8946 Rating:
|
Fuses blown on all 3 input - phases? Your SITOP seemed burned, replace it. |
Last edited by: IBN-Service at: 5/22/2011 8:54 AM |
|
5/22/2011 8:43 PM | |
Posts: 259 Rating:
|
Nice, maybe i would use your advice. Thank you for replay. With regards, makaveli |
This contribution was helpful to
1 thankful Users |
5/23/2011 1:38 PM | |
Joined: 3/21/2006 Last visit: 4/25/2024 Posts: 10228 Rating:
|
Hello, His idea was to find the reason/s for that burned SITOP eventually. I hope you checked already there. About the price of SITOP - because here according to the rules is not allowed to mention some numbers, I suggest you to take a look at CA01 Catalog 2011. (Hope you know russian language). Other ways - contact with Siemens or with me (send PM). Best regards, Hristo Mihalev |
This contribution was helpful to
1 thankful Users |
Follow us on