4/6/2013 6:04 PM | |
Joined: 3/28/2010 Last visit: 8/5/2024 Posts: 1051 Rating:
|
Good question. Whether "sequential ASCII text files" means the dump of an entire logger file, or, the periodic export of specified variables is not clear. No example is provided. To do so, the FST's RS-232 com settings have to be compatible with the serial printer setup the Logger has to be configured (which points, how often). The 'printer' mode is enabled separately under Logger Control > Output Logger. 2) Terminal Mode 3) Serial port connection to SiWare software SiWare software provides SiWare software is available as free download from Siemens, but as of March 2013, it is not included on the CD ROM that ships with the FST020. It was previously called DataView software. "Si-Ware software Ver. 1.01.02 for all SITRANS F US clamp-on ultrasonic flowmeters" SiWare connects to the FST-020 with a Null Modem DB9F x DB9M serial cable. 4) Logger memory The logger has a fixed amount of memory. The logger is configured for which data points are saved. Under Meter Facilities > Logger Control there is a calculated value for the estimated log time remaining (Est LogTime Left) in hours and minutes. 5) The obvious means of exporting real-time flow rate data from the FST-020 are the The totalizer output can be handled with a periodic pulse output from either the electromechanical relay or an open collector transistor; where each pulse represent X volume. |