Dear Sebass , the LR560 was developed for huge ranges, like 40m or 100m. Therefore, it is not the best choice for short ranges. I guess, that the response time for suchrapid processes, will not be high enough here. You can lock off some filters, like e.g. the Echo Lock for the not needed agitator, to make it more quick, but this will not solve your application. For a comparable application like e.g. a crusher, I would always go for ultrasonic. The LUT400 together with the XPS-10 wouldgive youa muchquicker response time. Also, the 4-wire FMCW radar LR460 will be muchquickerthan theLR560 here. By the way. PactWare is afree of charge software for theLR560. http://pactware.software.informer.com/4.0/ Here the link to the needed DTM of the LR560.http://support.automation.siemens.com/WW/view/en/60441214 Cheers Levelmans |