9/26/2008 4:32 PM | |
Posts: 487 Rating:
|
You can use 3rd party loadcells that are compatible, check link for manual section 4.4.5. For adjustments see chapter 5 http://support.automation.siemens.com/WW/view/en/22600601 Here is a link to some sample projects http://support.automation.siemens.com/WW/view/en/22605342 |
9/26/2008 4:37 PM | |
Joined: 1/4/2007 Last visit: 7/11/2024 Posts: 1134 Rating:
|
Hello, You can connect to a Siwarex MS module load cells, if the technical data of the Siwarex MS module are conform to the technical data of the load cells. You need to check the technical data of the load cells (see also the attached pdf-file):- The load cells must have strain gauge in 4-wire or 6-wire system - The load cell powering of the Siwarex MS module is 6 V DC - The minimum input resistance for the Siwarex MS module is 40 Ohm (attend also, if you are usingload cells in parallel connection) - The load cell characteristic must be1 mV/V ... 4 mV/V It is independent, if the load cells are from Siemens or not.
AttachmentSiwarex_MS_information.zip (371 Downloads) |
Last edited by: Siwarexi at: 9/26/2008 4:40 PM |
|
Follow us on