Hola Jefesson; Faiz favor, escreva-nos em ingles na sua proxima visita. Obrigado. Hello Jeffeson; Please write in English on your next visit. Since the IM 153-4 supports MPR for redundancy over Profinet, you do not need active bus modules for S7-400H systes as you would for Profibus. So the only reason to use active bus modulrs in ypur case would be for CiR (configuration in runtime, or remove/insert under power); is that what you are trying to do? In any case, the BM you are pointing to would be adequate for the 2 x 40mm SM modules . You would also need a BM PS/IM ( 6ES7195-7HA00-0CA0) for your IM 153-4 and your power supply unit. Both BMs must be integrated in a special deep-channel rack as described in this article. How many ET 200M bus modules can you mount on a deep ET 200M mounting channel? https://support.industry.siemens.com/cs/ww/en/view/109483722 Hope this helps, Daniel Chartier |