12/18/2014 12:39 PM | |
Posts: 8946 Rating:
|
Section is large enough but it must be also a screened cable! |
This contribution was helpful to
1 thankful Users |
12/18/2014 1:11 PM | |
Joined: 11/29/2011 Last visit: 7/17/2024 Posts: 1358 Rating:
|
Hi, I agree, voltage signals really sensitive for noise. Keep in mind the earthloops as described below! ![]() Anyways to extract from theS7-400 Automation System Module Data manual chapter 5.9: "Always use shielded twisted-pair cables to wire analog signals. This reduces interference. Connect both ends of the analog cable shield to ground. If there are potential differences between the cable ends, an equipotential bonding current, which can flow over the shield, can cause interference of the analog signals. To avoid this situation, you should ground the shield only at one end of the cable." Regards: |
- What you read here, please check with manuals and your requirements. |
|
12/18/2014 1:59 PM | |
Posts: 8946 Rating:
|
In proportion to the high input resistance of pot and voltage AI. voltage drop is less than 0.1% Just calculate yourself. Ohmsches Gesetzt |
This contribution was helpful to
1 thankful Users |
12/19/2014 4:32 PM | |
Joined: 6/13/2012 Last visit: 3/28/2024 Posts: 64 Rating:
|
Thank you for your answer, i just wanted an opinion . thank you |