6/7/2019 1:34 PM | |
Joined: 9/8/2011 Last visit: 8/7/2024 Posts: 537 Rating: (86) |
IF you are looking for the Real to be 12345678.0. check out this Article: https://en.wikipedia.org/wiki/Single-precision_floating-point_format |
A smart person learns from their mistakes |
|
6/7/2019 3:47 PM | |
Joined: 7/7/2010 Last visit: 10/7/2024 Posts: 15270 Rating: (2422)
|
Take a look at your input using the calculator found here: https://www.scadacore.com/tools/programming-calculators/online-hex-converter/ Pay attention to the datatype coercions matching the values you obtained. In FC1, you perform an explicit DWORD_TO_REAL which says these 4 bytes are actually real to start with, so please copy these bytes into this memory location and treat it as a real. In FC2, you perform an implicit DWORD to REAL by _assigning_ a DWORD to a REAL. Portal stuff the UINT32 into the real by figuring out the value in decimal, and then assigning that to a real. Hope that makes sense.
|
science guy |
|
This contribution was helpful to1 thankful Users |