4/3/2008 8:29 PM | |
Posts: 2661 Rating: (279) |
Did you create a Profibus network after inserting the CP 342-5? I tried and it works. See attachment. AttachmentDokument1.pdf (643 Downloads) |
4/3/2008 10:35 PM | |
Posts: 55 Rating: (1) |
This is what is configured in my netPro overview. |
4/3/2008 11:18 PM | |
Posts: 2661 Rating: (279) |
TheMisfit: I tried with a project exactly like your project (see attachment) and it works. See if it works for you with my project. If it does not, then there is something else wrong. AttachmentTest315.zip (651 Downloads) |
4/4/2008 2:05 AM | |
Posts: 55 Rating: (1) |
Hi Phantom75, Thanks for your reply. You project works fine, but I can't understand what is wrong with my own project. I've compared all settings. Could you take a quick look at the attachment? AttachmentPLCsim.zip (615 Downloads) |
Last edited by: TheMisfit at: 4/4/2008 3:24 PMLast edited by: TheMisfit at: 4/4/2008 3:22 PMLast edited by: TheMisfit at: 4/4/2008 3:17 PM |
|
4/4/2008 5:00 PM | |
Posts: 2661 Rating: (279) |
TheMisfit: I also could not access the 342-5 node in your project. Probably there is some sort of corruption in your HW Config data. Any way, the solution to your problem is, delete the CP and insert some other module (for example AI)and compile. Then delete the AI module and reinsert the CP 342-5 and compile again. Then you'll be able to see the 342-5 node in the PLCSIM. I tried this and it works. See attachment. AttachmentDokument1.pdf (677 Downloads) |
Last edited by: Phantom75 at: 4/4/2008 5:01 PMCorrected Typo. |
|