you have to check whether the motor should be connected in star(wye) or in delta connection, here is the connection schematics: Conn._________L1_____L2_______L3________Join Star(WYE)_____U1_____V1______W1______U2&V2&W2 Delta_______U1+W2___V1+U2___W1+V2___ ------- The 3 phaseoutput of the vfd (U,V,W)is then connected to the U1/V1/W1 terminals. Regarding the servo pump solution here you can find a lot more information incl. energy saving etc.: http://w3.siemens.com/mcms/mc-solutions/en/mechanical-engineering/plastic-machines/servopump/pages/servopump.aspx |