10/22/2018 10:51 AM | |
Joined: 5/12/2006 Last visit: 10/9/2024 Posts: 22405 Rating: (3017)
|
External encoder systems (except motor encoder) If, with DSC active, an external encoder is to be used, this requires the selection of a telegram with additional actual encoder values: Telegrams 6,106,116,118, 126, 138 or free telegrams. For optimum control in the DSC mode, the same encoder(s) (encoder 2 and/or encoder 3) must be selected for the control (master) and the drive via parameter p1192 "DSC encoder selection". If the encoder for the position actual value generation in the control and the encoder selected for DSC differ regarding their pulse numbers and/or fine resolution, then this must be taken into account in p1193. The factor represents the ratio of the pulse difference between the encoders used for the same distance reference. Further, it should be noted that for different encoders there are no dead times regarding their position actual value sensing (for example as is the case for EnDat encoders and SSI encoders), as this will otherwise lead to undesirable behavior. The effect of the parameters p1192 and p1193 is illustrated in function diagram 3090. https://support.industry.siemens.com/cs/ww/en/view/109754299 |
This contribution was helpful to1 thankful Users |
Follow us on