4/7/2014 3:58 PM | |
Joined: 1/2/2013 Last visit: 7/19/2024 Posts: 38 Rating:
|
Hello Mr. Cheetos7MC7511-1EA10-1CB7 comes with 2x PT100 in 3 wire connection. At the terminal of the sensor you will find the first one marked red, red and white and the second one marked black, black and yellow.One of them must be connected to TH200 7NG3211-1NN00-Z C11 and the other one to TH400 7NG3214-0NN00-Z C11. 7NG3130-0AB12-0AB12-Z C11 must be connected into the 4…20mA loop of TH200 (see attachment). TH400 comes with a reverse voltage protection. The measuring range of TH200 must be same like the measuring range of SITRANS TF. Otherwise you will have a wrong value at the display. The C11 certificates show you the ranges so you can take them for comparison.It will not be possible to place both transmitters inside the connection head of the sensor. Since you have chosen the high hinged cover there will be place for one transmitter inside the cover. The threads are available. |
Last edited by: Celsius at: 4/7/2014 4:08 PM |
|